Having read plumbingluddite's explanation of what had happened, I too decided to see if the sub-zero temperatures were the cause of my boiler failure.
After a couple of kettles of warm water down the outside of the condensate pipe and some gentle tapping I went inside and reset the boiler. It fired up first time, with no problems!
With a 3 month old baby in the house and being snowed in, this forum has got me out of a bit of bother, so thank you!
Cheers,
Chris
I've just hadthe same error code flash and even after defrosting the pipe running outside it wasnt happy.... so I removed the sump trap which was actually a very simple 4 screw job....only tip is to make sure you have a bucket under the boiler to catch the water that runs out for a minute or so...
Our sump was full of grey sludge and iron fillings.. wash it through..... bang it around to diss lodge them and even blow through hard with your mouth (outside)
Re fitted the sump and hey presto.... HEAT.....HOT WATER
and not a £100 call out plus labour charge in sight