Hi,
I've just replaced the pcb on our old icos he18 boiler and now its blowing the 2amp quick blow fuse in wiring centre (not the fuse in the Pcb). We tested fan resistance before changing and harness for earth leak/cross continuity. The PCB was replaced because the boiler was completely dead (no lights or activity).
I've checked all wires to PCB for earth fault. Gas valve shows 4.2k ohms across 2 wires. Flow thermostat seems to be ok as well with resistance decreasing with heat and within specs as per manual.
It doesn't appear to be externals causing the fuse to blow - when I switch on at the spur the pump runs with demand from hw cylinder stat. Moving the mid position valve manually also doesn't cause the fuse to blow.
It's only as the boiler starts it's ignition sequence that the fuse blows. I've pulled the gas valve and the spark gen connections and it still blows.
Pulling the flow thermostat and flue thermistor gives LE error on display and doesn't blow the fuse but it never starts the ignition sequence so I'm not sure this tells me anything. If I pull the connections to the overheat thermostat, the ignition sequence runs (I can hear the gas valve and the ignition sparking), the fuse doesn't blow but the boiler doesn't run due to stat being unplugged (gives LE on display).
Could it be the overheat stat causing fuse to blow? The other part that I can't eliminate is the flame detection because the ignition sequence doesn't run at all with this disconnected.
I don't want to start changing loads of parts with this boiler, I just want to keep it running for a few more months before it's replaced in the summer. i did try to get ideal to do a fixed price repair but they don't touch anything over 10 years old I realise we are probably lucky for it to have lasted as long as it has.
Any suggestions are much appreciated.
I've just replaced the pcb on our old icos he18 boiler and now its blowing the 2amp quick blow fuse in wiring centre (not the fuse in the Pcb). We tested fan resistance before changing and harness for earth leak/cross continuity. The PCB was replaced because the boiler was completely dead (no lights or activity).
I've checked all wires to PCB for earth fault. Gas valve shows 4.2k ohms across 2 wires. Flow thermostat seems to be ok as well with resistance decreasing with heat and within specs as per manual.
It doesn't appear to be externals causing the fuse to blow - when I switch on at the spur the pump runs with demand from hw cylinder stat. Moving the mid position valve manually also doesn't cause the fuse to blow.
It's only as the boiler starts it's ignition sequence that the fuse blows. I've pulled the gas valve and the spark gen connections and it still blows.
Pulling the flow thermostat and flue thermistor gives LE error on display and doesn't blow the fuse but it never starts the ignition sequence so I'm not sure this tells me anything. If I pull the connections to the overheat thermostat, the ignition sequence runs (I can hear the gas valve and the ignition sparking), the fuse doesn't blow but the boiler doesn't run due to stat being unplugged (gives LE on display).
Could it be the overheat stat causing fuse to blow? The other part that I can't eliminate is the flame detection because the ignition sequence doesn't run at all with this disconnected.
I don't want to start changing loads of parts with this boiler, I just want to keep it running for a few more months before it's replaced in the summer. i did try to get ideal to do a fixed price repair but they don't touch anything over 10 years old I realise we are probably lucky for it to have lasted as long as it has.
Any suggestions are much appreciated.