Hi there,
I hope someone can help.
I have an Ideal Isar 24 (yes I know they are rubbish ) - it was installed approx 3-4 years ago.
Until recently it's been working great - no issues whatsoever. At first I noticed the heating pipes were getting warm in the night, and hot water was warm not hot - so I checked and changed the diverter valve. The old one looked in fairly good condition but the shaft was sticking.
Now the diverter has been changed I no longer see the rads getting warm, but there is still a problem.
Most of the time the taps run warm to hot rather than very hot, or it takes a long time for the hot water to arrive. Occasionally there will be very hot water and them warm to hot water. The kitchen taps usually run slightly hotter than the taps upstairs.
Just now - when DHW was on, the water was coming out of tap very hot, I can hear the pump going and if I look at the CH pressure valve it's goes from a steady bar to slightly above, then drops to just below 1 bar and back to 1 bar again (I can hear the pump changing pitch when this is happening). The burner was running, stopped, water went warm, press remained at 1bar, burner started again, after 30s or so water was hot again and pump/CH pressure changing. CH outlet pipe remained cool when this was happening.
Could this be a blockage in the plate heat exchanger?
I guess it is not a thermistor problem because there are no errors whatsoever reported.
I have the old black PCB not the new orange one.
If I swap the plate heat exchanger is it worth also swapping the PCB out for the new one?
Any ideas appreciated!!
Thanks in advance
Matt.
I hope someone can help.
I have an Ideal Isar 24 (yes I know they are rubbish ) - it was installed approx 3-4 years ago.
Until recently it's been working great - no issues whatsoever. At first I noticed the heating pipes were getting warm in the night, and hot water was warm not hot - so I checked and changed the diverter valve. The old one looked in fairly good condition but the shaft was sticking.
Now the diverter has been changed I no longer see the rads getting warm, but there is still a problem.
Most of the time the taps run warm to hot rather than very hot, or it takes a long time for the hot water to arrive. Occasionally there will be very hot water and them warm to hot water. The kitchen taps usually run slightly hotter than the taps upstairs.
Just now - when DHW was on, the water was coming out of tap very hot, I can hear the pump going and if I look at the CH pressure valve it's goes from a steady bar to slightly above, then drops to just below 1 bar and back to 1 bar again (I can hear the pump changing pitch when this is happening). The burner was running, stopped, water went warm, press remained at 1bar, burner started again, after 30s or so water was hot again and pump/CH pressure changing. CH outlet pipe remained cool when this was happening.
Could this be a blockage in the plate heat exchanger?
I guess it is not a thermistor problem because there are no errors whatsoever reported.
I have the old black PCB not the new orange one.
If I swap the plate heat exchanger is it worth also swapping the PCB out for the new one?
Any ideas appreciated!!
Thanks in advance
Matt.