yes, tested with DMM, constant 240
At the boiler? When you switch controller between CH, DHW and both?
yes, tested with DMM, constant 240
double checked (infact about quadzillion checked !!) wiring in JBox for connections to mid pos, valves and room and tank stats, to boiler. all as per spec.
It seems to come back to flow when just CH selected, even though pump is powered and running aven though allm rads getting hot ?
nd system works fine as long as DHW is on, so what are thoughts.
Change pump
Can put say a small load between the boiler SL and N with CH only selected and boiler presumably not firing, something like a 50W "bulb" or the like and see do you still have 240V.existing system, new build from 12 years ago. As per original installation.
There is no mag filter
madrab - I totally agree something not right. I cannot get my head around there being a call ( c ) on boiler display whether on HW only or CH, and the boiler somehow differentiating c for CH only or c for DHW/DHW+CH
I agree that flow is sensible cause to investigate, which i have, in as much the live output to pump is correct and the pump is circulating when CH only is selected (assuming room stat is NOT satisfied), and SL at boiler is at 240V when c at display panel
However, the flow sensor must be working, otherwise burner light indicator would not stay on when CH + DHW is selected
i take your point of adding an additional load to verify