We must have been here before but - the springs for the plug may be 13A but the conductor terminals, surely, have to be 20A (for a ring).
Of course. In fact, more than 20A, since one doesn't have to have too unbalanced a load on a ring final for the current in one leg to exceed 20A. However, as I said, I thought we were talking about published 'ratings', and I do seriously doubt that you'll find a 13A single socket, or an FCU which the manufacturers say is 'rated' at more than 13A.
Back to the timer. I thought my interpretation was accepted/common practice for immersion heaters.
I actually thought the same about what I was saying - but it transpires that, by chance, it seems that I've only ever been exposed to immersion timers which were rated at 13A.
However - If rated at only 13A, does that mean the timer should be protected by a 13A fuse?
Well, that's someone that people might expect me to say - but,as you go on to point out....
I know, I know - the mcb protects the cable ...
...which is the response I usually get when I make such suggestions, but then you go on to say:
but the timer can be overloaded and, as such, should not be on a 16A circuit. As it is rated at 13A (not 16A) this would indicate that 13A is all it can handle.
Do I take it that I have a convert ?
Would you therefore have a problem with, say, 10mm² cable (clipped direct) on a 50A MCB supplying a 7.5 kW shower (provided you were not constrained by MIs)?
Alternatively, if it is acceptable to use a 13A fuse for an immersion heater then there is no reason that a 13A plug on a ring circuit cannot be used as with the 3kW kettle (albeit on for three minutes, though).
I think that '3 minutes' is probably crucial, and brings us back to the apparent deficiencies of BS1363 plugs/sockets. We often discuss the fact that double sockets seem unable (and may well not be 'rated' to) safely cope with a sustained load of 2 x 13A, but we discuss less the fact that a single plug/socket seems at risk of getting hot, if not worse, with a sustained 13A load.[/quote]
For some reason immersion heaters should be on a dedicated circuit and are usually wired with hugely oversized conductors.
I have always assumed that the reason for recommending dedicated circuits for high fixed (and often semi-continuous) loads was that socket circuits (which are probably the ultimate in a 'diversity' situation) were never really intended for such things, which effectively limit the capacity of the circuit to provide power to sockets - plus, as above, probably a feeling that plugs/sockets are not a good means of connecting a high sustained loads.