As you say, a 50Ω earth is not, in itelf, a problem - that's lower than many an earth rod in a TT installation provides. However, as I said, there is theoretically no guarantee that it will always be there - the water supply company could, one day, replace the water supply pipe virtually all the way up to your property with plastic - in which case you'd end up with little or no earth.From the 'safe' point of view I am not sure I understand why a 50Ω Earth would not be sufficient. In the event of a short between live and earth the RCD would trip, in the event of a person being the earth the RCD would also trip?
OK, so you are aware of this, so if you saw people with massive coils of plastic pipe digging holes outside of your house, warning bells would probably ring in your head. However, what if the house comes into different ownership?
I don't think that any electrician would, could or should do any work on your electrical installation if there was no 'proper' earth, compliant with current regulations - but I imagine that others will comment on that.
Kind Regards, John