Are you sure? An MCB will take an hour at that level.It will blow at higher current, the bigger the overload, the quicker it will blow. At about 45% overload it will blow pretty well instantly.
Are you sure? An MCB will take an hour at that level.It will blow at higher current, the bigger the overload, the quicker it will blow. At about 45% overload it will blow pretty well instantly.
... and JohnD If his "pretty well instantly" means less than 1 second, then it looks as if it would take about 500A to blow a 60A fuse that quickly. If he meant less than 0.1 sec, it would need nearer to 900A!This will surprise hard-work
No. But there is always a 1st time.Have you ever blown a 60A main fuse?
So a 60A fuse will only blow after 5 seconds if 330A is draw. Wow. I am not surprised as these I knew a long time ago and semi-forgot.This will surprise hard-work
I think that it's probably extremely unlikely due to overload in any normal domestic situation, particularly if there is no electric shower. When service fuses blow, it is usually due to a fault.No. But there is always a 1st time.
I will go with the 4mm flex heat resistant cable. I thought there must be a reason why TLC do not stock 6mm heat resistant flex cable. Like you, I do not like T&E to connect to appliances. It was not designed for that. It is for permanent installations. An oven is not a permanent installation as it is an expendable appliance that will need replacing at some time. Is there a reg stopping T&E connecting appliances?Yes, I would be happy to use that.
For what it's worth, I personally don't like using twin & earth to connect cooking appliances.
Kind Regards, John
At least in terms of things domestic, once one has taken diversity into account, I don't think you would find any usually-flex-connected load that would require bigger than 4mm². Showers will often/usually need bigger, but they are not wired in flex.I will go with the 4mm flex heat resistant cable. I thought there must be a reason why TLC do not stock 6mm heat resistant flex cable.
I'm not aware of any specific regulation that prohibits it. My main problems with it are those of practicalities - and, of course, it is usually not specifically 'heat-resistant'.Like you, I do not like T&E to connect to appliances. It was not designed for that. It is for permanent installations. An oven is not a permanent installation as it is an expendable appliance that will need replacing at some time. Is there a reg stopping T&E connecting appliances?
I personally really would not worry about that, but others might!One point about the TLC 4mm cable. It is rated to 85C not 90C. Maybe a 90C resistant sheath over it would do.
If there were concern about the heat tolerance of the cable (and, as I said the 5° difference would not concern me!), I'm not at all sure that putting it within heat-resistant sleeving would necessarily make much difference. The sheath would be able to tolerate a slightly higher temp, but would probably conduct that heat through to the cable within!TLC has heat resistant sheathing, at 88p per metre:
What are the manufacturer guaranteeing by specifying that cable? The appliance guarantee stops at the appliance terminals, if it was that important for the warranty then they would supply it pre flexed, or are they gonna insist on a 90degree cooker connection unit as well? A length of 2.5 or 4mm flex will be sufficient and perfectly safeThe makers specify `heat resistant` cable. Guarantee purposes. The 4mm is within range by 3A but it would be nice to have 6mm all the way.
I agree with you 100%. The sheath takes 155C. It must add some extra safety aspect. But guarantee issues may arise and they can be very funny about those. For about £1 for a sleeve all is solved on that point. The 155C will shut them up.If there were concern about the heat tolerance of the cable (and, as I said the 5° difference would not concern me!), I'm not at all sure that putting it within heat-resistant sleeving would necessarily make much difference. The sheath would be able to tolerate a slightly higher temp, but would probably conduct that heat through to the cable within!
Kind Regards, John