What you have done is failed to comply with BS7671. Simply put!
Regulation 701.415.2.
Supplementary equipotential bonding is required to connect together the protective conductors of each circuit supplying class I and class II equipment to accessible extraneous conductive parts, as listed.
Unless of course you are able to:
(i) Prove that all final circuits in the location achieve ADS in accordance with 411.3.2
(ii) Provide additional protection by means of a 30mA rcd
(iii) Prove that all extraneous conductive parts within the location are effectively connected to the protective equipotential bonding.
As a competent electrician you should really be aware of this