OK - it's the right size cable.I am only measuring it with my tape. I bought the cable at B & Q as lighting circuit cable. It's about half the thickness of the cable I got for installing a fused spur to a power socket, and about a third of the thickness of the cable to my electric Hob.
For the third time, that is wrong, and not allowed. You may not have a single-insulated cable running anywhere except within a containment system. Taping it to the other cable will not do - you must remove it and replace it with a sheathed cable.The single red wire I added from the light switch to the isolater, and on to the fan I taped to the other cable to keep them all together and labeled them as such, should someone else need them in future, and used the red one as it connects to the red at the light switch
You've got some of that - why did you make more work for yourself by pulling it apart to make it unsafe?
Use twin and earth from the switch to the isolator. Either terminate the unused core in choc-block at each end or sleeve it G/Y at each end and connect it to the earth.
Then use 3-core & earth from the isolator to the fan.
OR - as sparkwright says, if your lighting circuit loops through the light fitting, or a nearby JB, you'll have permanent and switched live and neutral in one place and you can use 3C+E from there to the isolator.
Doesn't matter - you must still maintain earth continuity in all of the cables. If the box that the isolator is in has no earth terminal then join the earths inside it with a piece of choc-block.The earth lead was connected to the earth in the light switch, but there is no connection for it in the isolator, or the fan.
At the fan terminate the earth with the same - don't just cut it back.
And you think they're all like that?Incidently, if your wondering why I just don't get an electrician to do this, the last one I had in, several years ago was installing my gas boiler. The plumber removed the old back boiler from the fireplace, installed connecting pipes and installed the a gas fire in front of it without tightening the pipes. the water soaked through both sides of the wall and the plaster fell off both walls. The electrician wired the heating thermostat to the motorised valve for the hot water, and the heating thermostat to the hot water valve. The hot water cylinder nearly exploded before I came home and worked out what was wrong.