Was it all working OK before the EP was removed?
At the end of the day terminal 4 from the EP becomes live when it the EP switches the heating on, terminal 3 of the nest does exactly the same thing. Have you checked that the red wires that were in the EP L and 4 are connected as below and not the other way around? Is terminal 2 connected to L?
The red wire from EP L ..... goes to Nest L
The red wire in EP 4 Central Heating on... goes to Nest 3 Heating call for heat
Was / is there an existing room thermostat, and if so what have you done to / with it?
Did anything happen during the fitting of the Nest when you were had the wires connected wrongly, fuse blown for example?
Can you explain what you mean by the following please?
Boiler had power but when you turn up the nest thermostat the boiler turns off.... No heat.
Are you saying that the boiler is running (ie firing) and when you turn the nest up the boiler stops firing? Is it possible that the boiler has shut down because of its internal thermostat, because there is little demand for heat (TRV's closed for example)
Is the hot water working OK with the Nest?
Have you checked that every wire has been moved as I described and all of the links are present, it's easy to miss one
Have you checked every terminal to make sure that the connections are secure and the conductors are clamped under the terminals not the insulation? Nests are fiddly beasts for those of us that are used to them. Bad connections are common.
Because you had a wire connected to terminal 1 of the EP, we have all assumed that you have a system with a 3-port motorised valve (aka Y-Plan) is that correct?
As
@The Novice asks, a photo might help.