Supply the lights from or in the same cable, as the indicators NOT the switches, there are no neutrals at the switches.I think I see what you mean about supplying the lights from the switches,
The indicators can off course be fitted next to the switches though.
The way you show on the drawing is 44m cu to last switch .38m back through indicators, and 38 m through the lights.
A whopping 120 metres
Not too keen to work it out exact tonight, but as a QUIDE only , from the drawing, your last light is approx 120 metres of cable,which is too much, due to volt drop and earth loop impedance .
I would start thinking of at least 1.5 mm with a 6amp mcb.
Regarding the Earth loop impedance, on site quide afaik says
1.0 at 6a may limit the cable to 38 metres
1.5 at 6a may limit the cable to 59 metres
This may vary with installation methods.
The amps you say 500watt so 2.17 amps
volt drop is I think 44mv/Amp/metre for 1.0mm and 29mv/Amp/metre for 1.5mm.
So
volt drop for 1.5mm is 29mv X 120met X 2.17 amps = 5664mv
divide by 1000 is 7.5 volts
And
volt drop for 1.0mm is 44mv X 120met X 2.17amps = 11.45 volts
Max volt drop afaik is 9.2 volts max, this is from the mcb to the last light.!
IMO, 1mm is pointless.
Think of the indicators as the lights and vise versa, you sound like you want to use twin and earth, therefore wire as 10 or so lights, as a radial starting at the first indicator as your drawing.
Forget the switch wires for now as you know how to wire them,
The lights and switches and indicator are close by each door i presume.
So run the 2core +e as a radial, from ind1 to light 1 to ind 2 ,to light 2, to ind 3 to light 3 etc, or similar.
This will reduce the run a lot , you need to aim for 60 metres max I think.
If poss redo your drawing the proposed wiring route including measurements.