My daughter bought a house in Somerset last year (2012) and had problems with the boiler losing pressure and needing frequent topping up.
The boiler is a Grant Outdoor Vortex Combi about three years old.
The previous owner had clearly had the problem and we have the plumbers bills to prove it! The pressure vessel, PRV (pressure relief valve), low pressure switch and even the filling loop had all been replaced by their plumber.
It was clear to me that the pressure was rising too high and being released by the PRV, (I put a container under the discharge pipe to prove it). Then, when the water cooled, the pressure dropped too low to enable the boiler to start up again. The PRV on this boiler is set to 2.5 bar.
I decided to put an additional pressure vessel in the system, putting it under the kitchen sink and connected to the return pipe to the boiler. I also fitted a pressure gauge and filling loop with it, so if the problem persisted, I wouldn't have to go outside to recharge it! I reasoned that it would be best to fit a larger vessel than is theoretically needed, so I fitted an 18 litre vessel (setting the air pressure to 1 bar). This was then in addition to the 10 litre vessel in the boiler.
This has completely cured the problem. The pressure now never rises above 1 bar, even when the heating is working all day. Since the initial charge it has not needed topping up at all.
p.s I am not a professional plumber, just a reasonably competent DIYer. You can buy the parts required fro
Screwfix or Tool Station etc., but I got the vessel, gauge, filling loop and a PRV as a kit on eBay for about £50. (The PRV was not needed as this already exists in the boiler).