is 28mm pipe required to supply gas to 25kw combi boiler?

Some gas engineer don't want to waste time do the calculations and just go for the bigger size (bigger job maybe?)

Last, but one, boiler swap, the engineer was insisting it needed a new pipe, run on the outside surface, all the way from the meter, around two walls of the house. It would look horrible. The new boiler, was a size down from the original, the pipework was all buried, and properly calculated at install. I redid the calcs, sent that potential installer packing, and found another. The 22mm pipe was fine for that install, and the subsequent one too.
 
Sponsored Links
The pressure drop, needs to be calculated, not guessed at. Some gas fitters just play safe and guess. What Kw of combi do you have installed at the moment?
Here's an online calculation. I'd expect it to calculate gas flow if you enter kW and gas type, but oddly, it doesn't and you have to enter a figure. Using a generous 2.5m3/h still gives well below 1mb.
 
A 25kw main combi uses 2.71m3
this can be achieved with roughly 22 metres of 22mm copper so unless you have an excessive amount of elbows in your 10 metre run then your existing supply should be ok
you allow 0.6m for a 22mm elbow .
Also you have to allow for any other appliances coming off the run
 