Why not make the Dual pole isolator FCU your switch.
I want a
timed fan. Would your suggestion not mean I either 1. Have to have the switched live unfused or 2. Have the lights inoperable when the FCU is switched off?
Cheers
Not looked for a while with the Tour de France and cricket to watch (well hide behind the couch) and a bit of work to do!
Sorry I didn't pick up on the fact that you were after a timed fan - clearly this won't work with an FCU alone.
I personally think the introduction of an FCU, especially on a lighting circuit, is a get out for the manufacturers if something goes wrong with the fan.
Another option, which complies with MI's and your requirements and keeps everything at the switch is to utilise the mini-grid system.
This will allow you to have a fused switch and three pole isolator in the same, albeit slightly larger, switch.
Bring 3 core and earth from the ceiling rose light, utilising the live (brown), and neutral (black) to the supply side of the fuse switch and take the grey(brown sleeving) back to the ceiling rose as switch live load - connect the earths.
Take 3 core and earth from the fuse switch to the three pole isolator(3PI) switch.
That is brown from the fuse switch supply live to the 3PI (in) permanent live.
The grey(brown sleeving) from the fuse switch (switch live load) to the 3PI(in) switch live and the black from the supply side neutral to the 3PI(in) neutral. Also run the earths as well.
Then from the 3PI(out) Live, switch live, neutral and earth to the timer fan.
You probably won't need the earth at the fan but it helps with testing.
This way you can have your fan on the timer or not on at all and your light linked to the fan or not at all. And I think it will comply with the MI's.