I have worked the outputs from the link you supplied (thanks very much).
It comes in at 40,646 BTU.
The system probably contains 100 lites of water, so if it is circulating, it should take more than a minute to bring this back to 80C or whatever, even without much heat transfer from the rads.
So the boiler is taking about an hour to get up to temp and then it is cycling - one minute ON, four minutes OFF.thomsob said:The boiler only seems to come on for 1 minute bursts after it has been on for an hour or so.
How long between the one minute on periods? 4 minutes.
As I have shown, the boiler is about 60% oversized. Even if there was no sludge etc in the system, the boiler will cycle.
for clarity, why will a 50 litre cylinder work when a 100 litre CH system doesn't?
Please don't be offensive. Just provide your explanation.
You may wish to include the two cyl stats you added to your original post after your snotty reply.
Please explain how and whyBigBurner";p="1083721 said:Then boiler cycling will be eliminated as the cylinder acts as a buffer.