My house is very long and narrow - 60ft from front to back. The supply comes in at the front of the house, into the meter in the cellar (PME earth), then into an MEM 100A ASN100R isolator installed by the electricity supplier and then into a service connector block. There are two sets of tails from the connector, one straight into a split load 11 way (6 used) consumer unit which services the main part of the house. The second set of tails goes into a 60A DP isolator (installed 20 years ago) from which 20mm (external size) twin & earth -about 40ft long - goes to a separate consumer unit feeding the kitchen at the back of the house. I have just replaced the old kitchen consumer unit with an MK 8 way split load (only the ring sockets are on the protected side). The new MK has the standard 100A isolator. Question - yes, there is one - do I need to replace the 60A DP isolator in the cellar and, if so, which make would be suitable. Any advice will be much appreciated, thanks.