Whilst investigating a query from a house that has solar panels relating to the voltage I came across some interesting facts in an ENA document.
The document is the Electricity Network Association recommendation
(GS 83 Recommendations for the Connection of Type Tested Small Scale (Up to 16A per Phase) in Parallel with Low-Voltage distribution Systems)
that all the DNOs follow.
It brings to light some points
1/ There is no need for people installing equipment to be approved to do so or to notify the DNO which must be done within 28 days of connection.
(though wiring between the DNO connection point and the output of the equipment needs to comply with BS7671)
2/ The declared voltage of 230V +10/-6 % only needs to be at that level at the DNO terminals, once on the premises it can go as high as 262.2V which is the first level that, say, an inverter has to trip.
(obviously it will always need to be higher than the network voltage to export power to that network)
3/ Rating is to be measure in amps with the maximum being 16A which equates to 3.68kW at 230V
The document is the Electricity Network Association recommendation
(GS 83 Recommendations for the Connection of Type Tested Small Scale (Up to 16A per Phase) in Parallel with Low-Voltage distribution Systems)
that all the DNOs follow.
It brings to light some points
1/ There is no need for people installing equipment to be approved to do so or to notify the DNO which must be done within 28 days of connection.
(though wiring between the DNO connection point and the output of the equipment needs to comply with BS7671)
2/ The declared voltage of 230V +10/-6 % only needs to be at that level at the DNO terminals, once on the premises it can go as high as 262.2V which is the first level that, say, an inverter has to trip.
(obviously it will always need to be higher than the network voltage to export power to that network)
3/ Rating is to be measure in amps with the maximum being 16A which equates to 3.68kW at 230V