One has to be very careful with centre tap. To use a centre tap all the control needs to be two pole. Switches, and any relay plus fuses. Although we do not fuse a neutral with centre tap it's not a neutral so line 2 does needs fusing.Though for increased safety ( or rather reduced risk ) I would centre tap the 110 volt secondary to earth and/or CPC of the 110 volt system thus limiting touch voltage ( relative to ground / CPC ) to 55 volts or less.
As to other safety features as with any item we must hope the manufacture gets it right. To buy a British version which will have passed British safety laws I would think is better than hoping the grey import has the safety built in. I would think there is no problem with Japan would be worried if made in China. However one would consider the same for German stuff. However German stuff for export does not have European safety features so unless one has bought it in Japan and personally shipped it here you have no way of knowing if designed the same as one for home market.