Hi folks. I'm currently involved with the refurbishment of a fairly large 3-story terraced late Victorian house.
It was re-wired (well, really 'wired', since the only 'electrical installation' previously there related to a few lights!) a bit over 20 years ago (pre 'Part P'), and generally seems to have been done pretty well, and with a surprisingly generous number of socket outlets in every room. Apart from a few minor matters of detail, all it probably needs ('in due course') is an upgrade to the CU.
There are just three sockets circuits (all 32A ring finals), one for each floor. That's clearly enough for the upper two floors. On the ground floor, just the one 32A circuit serves both the kitchen (& 'utility area') and the other two modest-sized 'reception' rooms on that floor. There is also a cooker circuit to the kitchen.
If I were designing the installation from scratch, I would undoubtedly have a 32A (radial or ring) sockets circuit for the 'ground floor' (reception rooms) and another similar for 'the kitchen', so I'm wondering whether I should be considering the addition of an extra circuit.
What are people's thoughts. I'm tempted to consider the one circuit as essentially just being a kitchen/utility circuit, with the other two rooms 'also supplied' by it since the only appreciable non-kitchen loads I image would be likely would be ('occasional') vacuum cleaner/carpet cleaner etc. and perhaps occasions electric heaters (fan heater or whatever), or maybe, occasionally, garden 'power tools'.
To some extent I can answer my own question, in that it would obvious, in some senses, be 'better, to have two circuits, but I wonder whether it's really necessary? What do folk think?
Kind Regards, John
It was re-wired (well, really 'wired', since the only 'electrical installation' previously there related to a few lights!) a bit over 20 years ago (pre 'Part P'), and generally seems to have been done pretty well, and with a surprisingly generous number of socket outlets in every room. Apart from a few minor matters of detail, all it probably needs ('in due course') is an upgrade to the CU.
There are just three sockets circuits (all 32A ring finals), one for each floor. That's clearly enough for the upper two floors. On the ground floor, just the one 32A circuit serves both the kitchen (& 'utility area') and the other two modest-sized 'reception' rooms on that floor. There is also a cooker circuit to the kitchen.
If I were designing the installation from scratch, I would undoubtedly have a 32A (radial or ring) sockets circuit for the 'ground floor' (reception rooms) and another similar for 'the kitchen', so I'm wondering whether I should be considering the addition of an extra circuit.
What are people's thoughts. I'm tempted to consider the one circuit as essentially just being a kitchen/utility circuit, with the other two rooms 'also supplied' by it since the only appreciable non-kitchen loads I image would be likely would be ('occasional') vacuum cleaner/carpet cleaner etc. and perhaps occasions electric heaters (fan heater or whatever), or maybe, occasionally, garden 'power tools'.
To some extent I can answer my own question, in that it would obvious, in some senses, be 'better, to have two circuits, but I wonder whether it's really necessary? What do folk think?
Kind Regards, John