Well I don't think people want to be clipping direct so I think we can see why rings are still used !
I know that's what you meant - but was adding an extra hypothetical 'idea' of my own!No, I meant two separate radials.I suppose that, at least in theory, a logical extrapolation from the 32A 2.5mm² RFC would be a 63A 4mm² RFC - but then I'm sure that people would then moan about the 'terminal ratings' of the accessories!
Buried in the wall counts as clipped direct.Well I don't think people want to be clipping direct so I think we can see why rings are still used !
I'm not quite sure what you mean - 'clipping direct' (in quotes!), aka Reference Method C, includes buried in walls etc - in fact, most 'common' installation methods that do not involve insulation or conduit.Well I don't think people want to be clipping direct so I think we can see why rings are still used !
Yep (AFAIAA), unless insulation is involved.does loose under floor count is clipped direct ?
That's arithmetically true, but stating it as you have makes the difference sound a lot more dramatic than it actually is.As to ring / radial with a ring you can use 106 meters of 2.5mm cable and be within the volt drop allowed using a 32A MCB but with a radial dropping to a 20A MCB the maximum length is just 32 meters which is why the idea of splitting a ring into two radials does not work.