If you followed that test exactly and didn't just measure end to end resistance of L, N and CPC then that's a step forward.
You now need to confirm conductor sizes and if any cables pass through any thermal insulation or are housed in trunking or conduit.
Each cable on a 30/32A ring final should have line and neutral conductors not less than 2.5mm (apart from MICC and must be capable of carrying a minimum of 20A under their installed conditions.
You now need to confirm conductor sizes and if any cables pass through any thermal insulation or are housed in trunking or conduit.
Each cable on a 30/32A ring final should have line and neutral conductors not less than 2.5mm (apart from MICC and must be capable of carrying a minimum of 20A under their installed conditions.