Eh? What shed and what socket supply? This thread is about MWCs and testing, isn't it?Hi, what's the supply to the shed ? It looks like 2.5mm but the socket supply looks like 4mm ? Do you have RCD protection on the supply ?
Fair enough (the Yellow book says the same). As I said, I wasn't certain, but also that it didn't make any difference to this discussions, since there is certainly no doubt that the regs require the testing - and it is the inability/failure of most DIYers to do all of that (which, in turn, may lead to the absence of a certificate) which is being discussed here.Green book 632.3? ... "The person of persons responsible for the design, construction, inspection and testing....... shall, as appropriate, give to the person ordering the work a Certificate........... together with the schedules described in Regulation 632.1" ...I'm not certain that BS7671 compliance actually requires that a certificate be handed to the customer, but it certainly requires that the testing should be done (and presumably recorded on an appropriate certificate). If (most unlikley) the testing has been done, a DIYer can complete the cert and then hand it to him/herself!
It requires that in such circumstances as a certificate is required to be issued, the said certificate must be handed to the person ordering the work.I'm not certain that BS7671 compliance actually requires that a certificate be handed to the customer, but it certainly requires that the testing should be done (and presumably recorded on an appropriate certificate). If (most unlikley) the testing has been done, a DIYer can complete the cert and then hand it to him/herself!Doh! What I mean is; until last week if I called in an electrician and did not get a MWC, I would not have known any difference. I.e. While I know testing has to be done to ensure safe operation and what it entails, I did not know the customer receives a copy of the results and the details regarding the job.
Kind Regards, John
I have to very shamefully admit that because I don't have a loop tester, When ever I have needed to know Zs in the past, I have calculated it based on a measured R1+R2 + a maximum of 0.8 Ohm for my TN-S earthing system. Not at all acceptable I know, but better than nothing. Will one day get a loop tester and check everything though.
Given that it is all-but-impossible that the DNO would state a Ze for TN-S which was greater than 0.8Ω, if using such a conservative estimate resulted in a satisfactory calculated Zs, I would say that is is no worse than 'enquiring' about the Ze. However, whether one 'enquires' or uses the conservative 0.8Ω figure, there remains the problem that that approach will not have confirmed that the CPC of the circuit is actually connected (satisfactorily) to the TN-S earth - so the Zs of the circuit could theoretically be 'infinity'!... there is nothing particularly wrong with that approach other than that the Ze should have been established by Enquiry from the DNO rather than just assuming it to be be 0.8 Ohms.I have to very shamefully admit that because I don't have a loop tester, When ever I have needed to know Zs in the past, I have calculated it based on a measured R1+R2 + a maximum of 0.8 Ohm for my TN-S earthing system. Not at all acceptable I know, but better than nothing. Will one day get a loop tester and check everything though.
The maximum impedances quoted are assumed in BS 7671 guidance. The DNOs do not work to BS 7671 or any of its associated guidance.Given that it is all-but-impossible that the DNO would state a Ze for TN-S which was greater than 0.8Ω, if using such a conservative estimate resulted in a satisfactory calculated Zs, I would say that is is no worse than 'enquiring' about the Ze.
Eh? What shed and what socket supply? This thread is about MWCs and testing, isn't it?Hi, what's the supply to the shed ? It looks like 2.5mm but the socket supply looks like 4mm ? Do you have RCD protection on the supply ?
Kind Regards, John
Did you perhaps have something to say?Eh? What shed and what socket supply? This thread is about MWCs and testing, isn't it?Hi, what's the supply to the shed ? It looks like 2.5mm but the socket supply looks like 4mm ? Do you have RCD protection on the supply ?
And when someone decides to make a claim, alleging that you left an installation unsafe. What evidence have you got/given to defend yourself with. I perform tests and issue certs, on everything I do once I have done work on the system, fair enough takes a little more time on the minor jobs, but covers my arse. I even take photos, if I have concerns/issues about the work I am being involved with.And it does not really matter if results are written down it's the testing that matters.
Quite so, and that's the problem with any sort of self-certification or self-policing - it relies totally on 'trust'.... in real terms if I go into a house I have tested so many times I could easy fudge up some results which look reasonable. So unless you have some one to sign to say they watched you taking the readings any bit of paper is useless it is simply your word against theirs.
If the typed up version correctly reflects what was written on the fag packet then, if there is any can to be carried, it surely must be carried by whoever did (or claims to have done) the tests and wrote the results on the fag packet? However, as above, in the absence of 'witnesses', the difficulty is in proving whether what was written on the fag packet was 'correct' (or, at least, an honest reflection of what readings the test instruments gave) or, indeed, if any testing was actually done.So if you test and write the results on your fag packet. Then in the canteen transfer them to some better paperwork. Then the office types them up and sends them to the client and there is an error who carries the can?
That would obviously require everyone who completed EICs or MWCs (including DIYers) to have equipment that many don't currently have - and, in any event, would still be open to abuse by those with some technical savvy!But the absence of any proof is worse! Even having a witness would not really improve things, maybe a print-out system of time, dated results directly linked to the test equipment could be a way forward.
We could require a new generation of testers, GPS & NTP enabled, tamper-proof audit logs, results encrypted with test equipment manufacturer or scheme organiser public keys, and they physically issue the certificates.That would obviously require everyone who completed EICs or MWCs (including DIYers) to have equipment that many don't currently have - and, in any event, would still be open to abuse by those with some technical savvy!
Indeed we could - but your 'spoiler' says it all. However, random checking of things that rely heavily (or totally) on trust is a very reasonable, and very standard, practice.We could require a new generation of testers, GPS & NTP enabled, tamper-proof audit logs, results encrypted with test equipment manufacturer or scheme organiser public keys, and they physically issue the certificates.That would obviously require everyone who completed EICs or MWCs (including DIYers) to have equipment that many don't currently have - and, in any event, would still be open to abuse by those with some technical savvy!