light breakers

Joined
6 Apr 2012
Messages
2
Reaction score
0
Country
United Kingdom
i have upstairs and downstairs lights on separate 5 amp breakers is it possible to put them both on a 10 amp breaker to free up space for a breaker for a under sink heater which has to be on a 30 amp :?:
 
i have upstairs and downstairs lights on separate 5 amp breakers is it possible to put them both on a 10 amp breaker
Yes you can though you would probably be in breach of the current regulations.

to free up space for a breaker for a under sink heater which has to be on a 30 amp :?:

It is highly likely that you will need to accompany the 30 Amp breaker with an RCD - see manufacturers instructions for the under sink heater they now all say that the RCD Must be fitted. Certainly redring and heatsave under sink heaters do - I am fitting two of these next week to holiday cabins.
In which case, assuming, your current board doesn't have any RCD protection, you will need a small RCD protected consumer unit solely for the use of the heater together with 6mm2 and 32Amp MCB or 40Amp MCB depending on the size of the heater 7.5 (32Amp) 8.5/9.5 (40Amp).
This will allow you to leave the lighting circuits alone.
This work is notifiable in England and Wales.
 
What "riveralt" has said is correct I will expand a little. The regulations state up to 16A on lighting but also it stated must comply with manufacturers recommendations and most ceiling roses are rated at 5 amp so this often results in real terms that a 5/6A MCB/RCBO/Fuse is required.

There are ways around it for example fused connection units but in the main 5A is enough today for all lights as use of low power bulbs has dropped the lighting load.

The other problem is safety and should a MCB/RCBO/Fuse open one much consider how one would fair. A risk assessment are there table lamps etc which could be easy switched on if the MCB/RCBO/Fuse should open.

Sinks are normally found in bathrooms and kitchens and in both cases Part P means in the main to DIY is very expensive compared with using a scheme member electrician. For some reason a utility room does not have same rules. However there are so many options likely it would still be better not to DIY.
 
thanks for the replies have post a pix of the consumer board lighting breakers up and down are second an third from the left i think this will give you some idea what iv got p.s was told by electrition it would cost £110 to put breaker in and isolator switch to the under sink heater that is only 18 foot away from the sink does this seem a far price
 
It would help if the photographs were in focus.
What kw size is your water heater?
 
Am I seeing that rights as a combined RCD/Main Switch - that's 4 modules wide ?

Possibly scope for swapping that out for something a bit more modern (2 modules wide) and making room for a couple of extra breakers ? On the other hand, by the time you've done that, got a longer live busbar, etc - you'd be a long way towards a complete CU swap.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top