No, your earth is obtained by the rod in the floor (the neutral side of their transformer is connected to a rod at their end), but the impediance of such a connection is higher than the types of earth provided directly (TNS - Supplier gives you earth wire, TNCS - Supplier gives you an earth from the neutral)
This means that you need an RCD on all circuits to disconnect in the event of an earth fault, now it looks like the main board is thus equipped, but there seem to be other boards connected via service blocks which don't seem to be.
The problem you are having is most likely down to the earthing rod having a much higher impedance than normally allowed even for a rod, this may be down to it being located under the floor instead of outside
If you talk to your supplier, they might be able to provide you with a TNCS earth
This means that you need an RCD on all circuits to disconnect in the event of an earth fault, now it looks like the main board is thus equipped, but there seem to be other boards connected via service blocks which don't seem to be.
The problem you are having is most likely down to the earthing rod having a much higher impedance than normally allowed even for a rod, this may be down to it being located under the floor instead of outside
If you talk to your supplier, they might be able to provide you with a TNCS earth