Extension of an existing lighting circuit -
Can one run two sets of 4 x 50w downlights off a radial extension from the lighting circuit on 1mm T&E.
Assuming all regulations on supply size and protections of course you can.
for the switch the wiring will be less than 50mm below the surface but within the safe zone, does this need earthed conduit to protect it?
That is one method but there are other methods as well BS 8436 cable for example.
The cable will be attached to the joists above 100 mm of insulation below 150mm more, is this acceptable?
As long as normal 5/6 amp protections is used yes.
Extra sockets
Please can you confirm that i am ok to run 3 Double sockets on a spur with a 13a FCU protecting them.
Actually thinking about it i could split the ring at the back of a double socket, replacing it with a single then extend the ring around this new room, are there suitable single gang accessories for this purpose?
There are double single backing boxes and if you download BS 7671:2008, Corrigendum (July 2008) from http://www.theiet.org/publishing/wiring-regulations/updates/ you will see what is allowed at end of document.
Also I believe all of this work does not need Part P as it is an extension of an existing circuit which is permitted.
Except for special locations and kitchens see http://www.planningportal.gov.uk/england/professionals/en/4000000001253.html to down load and read yourself it is in plain English.
I am also planning on putting in another spur on the ring in another location that originates from the kitchen but terminates in another room, would this be notifiable?
Most likely not but read yourself.
Also remember even if you don’t need to notify the LABC you should still test all circuits if you fill in the forms found in the Part P document or BS 7671:2008 forms from http://www.theiet.org/publishing/wiring-regulations/forms/index.cfm
Eric
Extra sockets
Eric