My house has a solid ground floor, and when I was replacing some unswitched sockets with switched ones downstairs, I noticed that they were all wired as spurs, with the cable dropping down conduit buried in the walls. When I lifted some floorboards upstairs I found that the sockets up there are on a proper ring (well, all the ones I checked were), and then single runs of cable are teed off from junction boxes or the sockets to go downstairs.
Does that describe it understandably? Shame I can't post a diagram.
Anyway - is this OK? Or should they all be on a proper ring? It's 2.5mm cable throughout, so just not quite enough, in theory, for a spur to a double socket, although in practice of course the chances of me running 2 x 13A appliances off one of the sockets is smaller than a small thing that's very small. But I imagine the regulations would say that if it can be done it must be safe....
The problem is that there isn't room in the conduit that's there for two pieces of 2.5mm cable. I haven't tried, but there is probably room for 4mm, which could safely carry the theoretical 26A, if that method of supplying the sockets is OK. Also if I removed the outer sheath from some 2.5mm I could probably get the individual wires down them to make a ring.
Another factor to think about is how long the ring would then be - it's only a typical 3-bed 1950s suburban semi, but if the ring went up and down the walls several times could it get a bit too long?
Dunno what's best - simplest thing would be to replace the drops with 4mm - I really don't want to have to rip the walls apart to put in bigger conduit.
Any advice?
Does that describe it understandably? Shame I can't post a diagram.
Anyway - is this OK? Or should they all be on a proper ring? It's 2.5mm cable throughout, so just not quite enough, in theory, for a spur to a double socket, although in practice of course the chances of me running 2 x 13A appliances off one of the sockets is smaller than a small thing that's very small. But I imagine the regulations would say that if it can be done it must be safe....
The problem is that there isn't room in the conduit that's there for two pieces of 2.5mm cable. I haven't tried, but there is probably room for 4mm, which could safely carry the theoretical 26A, if that method of supplying the sockets is OK. Also if I removed the outer sheath from some 2.5mm I could probably get the individual wires down them to make a ring.
Another factor to think about is how long the ring would then be - it's only a typical 3-bed 1950s suburban semi, but if the ring went up and down the walls several times could it get a bit too long?
Dunno what's best - simplest thing would be to replace the drops with 4mm - I really don't want to have to rip the walls apart to put in bigger conduit.
Any advice?