If you mean 'Safety Electrical Connection - Do Not Remove' there should be one.Does anyone put a warning notice next to an earth block these days or am I reading the reg wrong
If you mean 'Safety Electrical Connection - Do Not Remove' there should be one.Does anyone put a warning notice next to an earth block these days or am I reading the reg wrong
It's the other way round - tails sized by the fuse.I made the STUPID assumption that the size of the line/neutral tails would determine the maximum capacity of the incoming fuse and thus the maximum prospective fault current
The earthing conductor would have to be able to handle all of the PEarthFC.before the fuse would blow, and that the main earthing conductor had to handle half of this prospective fault current.
Adiabatic equation as in this: http://niceic.com/en/account/media/17thpg15.pdf[/QUOTE]
Yes.
If you mean 'Safety Electrical Connection - Do Not Remove' there should be one.Does anyone put a warning notice next to an earth block these days or am I reading the reg wrong
It's the other way round - tails sized by the fuse.
Well, yes you would hope so.I mean if it's a 10mm tail, you know the incoming fuse will not be a 80A or 100A as 10mm is rated for 65 Amps.It's the other way round - tails sized by the fuse.
Does anyone put a warning notice next to an earth block these days or am I reading the reg wrong
Because 16mm is required for pme supplies they hear rumours that you have to use 16mm for the main earth
Yep, I inherited one, and still have it (why not? ). Mind you, to be fair, it does need to be at least 4mm² if not mechanically protected. One certainly doesn't need to undertake any adiabatic calculation - even 1mm² cable would presumably be more than capable of carrying for an indefinite period of time the greatest current you could get down the average domestic TT electrode - so the limiting factor is the minimum 2.5/4.0mm² requirement of the regs!I've seen TT supplies with 16mm main earth when all that's required is a 2.5mm
If you are talking about the earthing conductor, that is not the case.Because 16mm is required for pme supplies
They do, as is the fashion for 25mm² tails regardless of the fuse rating.they hear rumours that you have to use 16mm for the main earth and start installing it everywhere without actually learning if it's required.
BS7671 states as above - paying safe is not really the reason.So is the advice in the book that defines what BS1671 says not quite correct or is everybody just playing safe?
That's all true, but neither the adiabatic calculation nor the lazy use of Table 54.7 are totally straightforward in the case to an earthing conductor. In terms of calculation, given that one doesn't know what protective device the fault current will be flowing through, I suppose one has to calculate on the basis of the circuit and device in the installation which gives the largest I²t. In terms of the point DaftPunk made about TT, as I said, an adiabatic calculation is really not necessary if the cable is able carry the PEFC continuously, but if one did want to undertake an adiabatic calculation, I suppose one would have to do it per the characteristics of an RCD?(which would result in a ludicrously small 'minimum CSA', which would be over-ridden by the 2.5/4mm² minima imposed by the regs)If you are talking about the earthing conductor, that is not the case. ... The earthing conductor (and CPCs) is always calculated by the adiabatic equation. ... Table 54.7 is only for use , as it states, "When it is desired NOT TO CALCULATE... ...in accordance with 544.1.3" (the equation).Because 16mm is required for pme supplies
That's it, then.That's all true,If you are talking about the earthing conductor, that is not the case. ... The earthing conductor (and CPCs) is always calculated by the adiabatic equation. ... Table 54.7 is only for use , as it states, "When it is desired NOT TO CALCULATE... ...in accordance with 544.1.3" (the equation).Because 16mm is required for pme supplies
Why not?but neither the adiabatic calculation nor the lazy use of Table 54.7 are totally straightforward in the case to an earthing conductor. In terms of calculation, given that one doesn't know what protective device the fault current will be flowing through,
For the earthing conductor, won't it be the main fuse?I suppose one has to calculate on the basis of the circuit and device in the installation which gives the largest I²t.
The earthing conductor is a CPC.As for those who want to use Table 54.7, that table was designed for CPCs, rather than earthing conductors, so one has to make an executive decision as to what to regard as "the associated line conductor" - I guess that would have to be the incoming supply conductor (in which case it's pretty likely to result in the magic 16mm² figure for the earthing conductor).
Well, as I said, mathematically it will be the 'circuit (path) and device which gives the largest I²t'. I suppose that we would usually be talking about the cutout fuse, but even that will often pose a problem for the designer, who often will not know for sure what size fuse is in the cutout!For the earthing conductor, won't it be the main fuse?I suppose one has to calculate on the basis of the circuit and device in the installation which gives the largest I²t.
Not per BS7671 definitions it isn't!The earthing conductor is a CPC.As for those who want to use Table 54.7, that table was designed for CPCs, rather than earthing conductors, so one has to make an executive decision as to what to regard as "the associated line conductor" - I guess that would have to be the incoming supply conductor (in which case it's pretty likely to result in the magic 16mm² figure for the earthing conductor).
Agreed, and I only mentioned it because you, in turn, had mentioned it as an alternative to calculaion.I don't understand why anyone would want to use 54.7 - it is merely a cover-all figure ...
It will - that's what the Table is designd for.- but you seem to be mixing two statements. If for CPCs then won't it be the evident circuit line conductor?
As I said, that's what I 'guessed' (i.e. assumed)If for the earthing conductor then the incoming cable.
It's people (including a good few electricians), not Table 54.7, that have "the magic 16mm²" in their heads. I suppose I shouldn't second guess the behaviour of DNOs, but I was assuming that 'S' (for incoming supply) would not normally be less than 16mm² - in which case the minimum CSA for an earthing conductor would, per 54.7, be 16mm² for any incoming cable size up to 35mm².54.7 does not have magic 16mm²; there is also an 'S' for line conductors of less than 16mm².