This morning I noticed that the main consumer unit RCCB (Crabtree 63A 30mA trip)was off. It would not reset until I had switched the CB for the kitchen power points off. When I switched the Kitchen CB back on, the RCCB tripped again. I then unplugged everything in the kitchen and got all circuits working.
On plugging stuff back in, I found a plinth heater, the kettle, and the washing machine, when plugged in individually, each tripped the RCCB. I then tried the kettle in a couple of lounge power points (a different circuit to the kitchen) and all was fine.
After scratching my head I used an extension lead to try the washing machine (the washing machine was the only appliance which had been operating this morning) from the same two power points in the lounge and the RCCB tripped both times.
Though the washing machine may seem to be the main culprit, the fact that the plinth heater and the kettle also trip the RCCB would seem to indicate that it is not.
I have removed the front of the consumer unit and visually inspected the RCCB - It looks fine/no smells of burning.
Could it be that the RCCB may have developed an enhanced sensitivity?
Any confirmation (or debunking) of my theory welcome.
Chris
This morning I noticed that the main consumer unit RCCB (Crabtree 63A 30mA trip)was off. It would not reset until I had switched the CB for the kitchen power points off. When I switched the Kitchen CB back on, the RCCB tripped again. I then unplugged everything in the kitchen and got all circuits working.
On plugging stuff back in, I found a plinth heater, the kettle, and the washing machine, when plugged in individually, each tripped the RCCB. I then tried the kettle in a couple of lounge power points (a different circuit to the kitchen) and all was fine.
After scratching my head I used an extension lead to try the washing machine (the washing machine was the only appliance which had been operating this morning) from the same two power points in the lounge and the RCCB tripped both times.
Though the washing machine may seem to be the main culprit, the fact that the plinth heater and the kettle also trip the RCCB would seem to indicate that it is not.
I have removed the front of the consumer unit and visually inspected the RCCB - It looks fine/no smells of burning.
Could it be that the RCCB may have developed an enhanced sensitivity?
Any confirmation (or debunking) of my theory welcome.