Do you mean that you have balanced the rads to give a 22C drop?
Yes that’s what I meant.
was motorized valve open to allow a flow through the radiator circuit?
No
Presumably you did the test with the pump on speed 3. What happens if you use speed 2? What temperature difference do you get when you do exactly the same test?
Yes I didn't ever attempt any other setting than 3 on the pump. I’ll check 2
Then I started considering the heat loss in the pipes on the primary circuit ... the loss would be about 1.2kw for an uninsulated 20m run 22mm at 55 degrees. Would that affect the temperature?
Of course! If there was no heat loss, the flow and return temps would be the same!
But what I am thinking is – would the system ever make the design 9 degree drop with such a huge primary circuit and a largish head?
I set the gate valve to a turn open as per the boiler manual and balanced the system at 22 degrees drop. This setting provides 1.1kw more than the loss of the house. This gave 15 - 16 degrees drop at the boiler.
If I open the gate valve more (attempting required 9 degree drop), there isn't enough pressure in the system to feed the radiators. If I open the rads to try and get 11 degrees, same problem, not enough pressure.
As I said before, the 15/60 is not up to the job.
I see your point…
I am thinking about installing the old 15-50 in the cellar and relocating the bypass so that it is, just after that. That would bring the head in the primary down to about 2.5m which is well within the capacity of that pump. I need to recalculate everything again to study the feasability. It looks like my calculations were pretty accurate from these results. I think I need to find a reputable engineer (as opposed to a plumber) to have a mark 1 eyeball at some stage.