The current in each leg is divided up in proportion to the leg length of a ring, if you put a 10A load in the middle, you'll get 5A down each side, move it to a quater way around and you get 7.5A and 2.5A, if its only a 10th of the way around you get 9A and 1A. You can't have a 30A load on a BS1363 plug obviously, but if you had 3 sockets clustered towards the end of the ring and had a 10A load on each then you could see the current divided up as something like 27A and 3A (if you had them a 10th of the way around), its almost as bad as a broken ring (where the ring accidentally becomes split somewhere along its length and is not a ring anymore)
When installing a ring, you should be careful to spead the sockets and loads out pretty evenly, no good wireing each one in turn, ending up 30m away from the fuse and putting a cable with no sockets on in to order to complete, much better to to get every second socket on the way out, and the remaining half on the way back