Hi
Can't find the answer to this in my DIY bible. Would be very grateful of your expert knowledge.
My shower has died, and I will head out tomorrow to purchase a replacement. The existing shower is 7kW, but I would like to replace it with maybe an 8.5kW. The existing cable is 10mm and runs aprox 4m to the consumer unit (2m of that is in stud wall with insulation). The existing MCB is B 32, with the main RCD being 80A, 30mA. I believe that for an 8.5kW shower I would need to upgrade to a 40 amp MCB? However, I have a nagging suspicion that I once read the maximum on an 80A RCD is an MCB of 32A.
Could anyone confirm if this is correct? Or if Im being dumb.
Many thanks
Can't find the answer to this in my DIY bible. Would be very grateful of your expert knowledge.
My shower has died, and I will head out tomorrow to purchase a replacement. The existing shower is 7kW, but I would like to replace it with maybe an 8.5kW. The existing cable is 10mm and runs aprox 4m to the consumer unit (2m of that is in stud wall with insulation). The existing MCB is B 32, with the main RCD being 80A, 30mA. I believe that for an 8.5kW shower I would need to upgrade to a 40 amp MCB? However, I have a nagging suspicion that I once read the maximum on an 80A RCD is an MCB of 32A.