Aren't the up-front RCDs all S type?
AFAICS, historically they've all been 100mA Type S - but I'm not sure I understand how any of that arose. As I said, once it's Type S, there's no point in having >30mA in the hope that it will produce some sort of discrimination (which it probably wouldn't, anyway). Furthermore, AFAIAA, these 'historical practices' for TT installations arose before there were (m)any downstream RCDs, so even the time-delay (and certainly not the 100mA) wasn't needed at that time. However, the moment one has downstream RCDs/RCBOs, one needs a TYpe S, but I don't really see why it needs to be 100mA, rather than 30mA.
These, as you know, cannot be used to protect (new) buried tails.
Sure, even if 30mA, a Type S RCD is no good for protection of persons. As soon as there are any downstream RCDs/RCBOs (which, these days, there usually will be), one obviously needs any upstream RCD to be time-delayed - so, as you say, in that situation the upstream one would not be adequate to protect buried tails (becasue it was Type S).
Plus, of course, it would be particularly silly with a 'top of the range' all RCBO board to have an up-front 30mA device.
I don't think that it would be any more silly with a 30mA than with a 100mA one, but I agree that it would be silly to have a regular (i.e. not time-delayed) RCD up-front. However, as I've said, if there are long distribution circuits/tails to be protected against L-E faults in a TT installation there would, AFAICS (and as with my installation), be a need for a (30mA or 100mA) time-delayed RCD up-front, even with your all-RCBO CU. However, as per the next paragraph, your all-RCBO CU might well be non-compliant with 314 if there had to be
any sort of up-front RCD,
unless all those RCBOs were DP!! ....
.... As previously discussed, there is a potential problem (and I confess I have two or three examples) if one has an up-front RCD (to protect tails/distribution cables) and any SP RCBOs protecting final circuits - since a N-E fault on a final circuit can then take out the whole installation (well, one whole phase, in my case) - arguably in violation of 314.
FWIW, for the first decade or so I was in my present house, with no RCDs in any of the CUs, the entire TT installation was protected by an up-front 30mA 'regular' (
not Type S) RCD for each phase, the previous 4-pole VOELCB having been ripped out soon after I first walked through the door
Kind Regards, John