Indeed, but that's almost identical to the fact that the BS7671 tabulated CCC's apparently take on board (i.e.include a margin for) the fact that a Type B MCB can carry 1.45 their In for up to 1 hour - so that can't explain the difference.Well if we take the fusing factor of a 100A cut-out fuse as 1.47, it is apparent that tails will need to carry at least 147A for a period without failing. The same will apply to any cable as we don't want cables failing before fuses/MCB's operate on load.
Kind Regards, John.