Minor leak Baxi 80e combi

Joined
15 May 2009
Messages
915
Reaction score
216
Location
Cheshire
Country
United Kingdom
Hi,

I'm a recently qualified gas engineer and was called out to the above boiler that had a very minor weep on the divertor valve where the diaphragm spindle comes through the gland nut where the micro switch is attached. Is it simply just a case of renewing this part (Baxi Diverter Valve Stuffing Box/Gland) or is it a case of renewing the diaphragm as well under the assumption the spindle may be worn? The functionality of the boiler is all O.K.

Many Thanks



Sloaney
 
Sponsored Links
Just replace gland seal / stuffing box. Usual fault on the carp baxi produce.

Take 10 mins at most.
 
for what it costs, I'd change microswitch, diaphragm and stuffing box. think there's a kit. No point getting called back for something that "was alright before you touched it mate" ;)
 