Just carrying out my minor job today for NIC assessment. I've added an extra socket (spur). I've got 2 questions.
1. Where is says RCD on the cert. I've filled in the BS(EN) no. & the In bit. What do I put in the "type". There was nothing written on the RCD saying what type so I put in 63A. Is this correct ?
2. I did my IR test. P-E & N-E was >299Mohms. I got 0.98Mohms on P-N but when I connected P&N together & measured across to Earth I got >299Mohms. I thought everything was unplugged but the house owner wasnt there & I wanst sure if an outside light had been spurred off a socket or something silly like that. Is this ok to put 0.98Mohms in the box & put a note saying P-N joined & tested across to E gave a >299Mohm reading.
1. Where is says RCD on the cert. I've filled in the BS(EN) no. & the In bit. What do I put in the "type". There was nothing written on the RCD saying what type so I put in 63A. Is this correct ?
2. I did my IR test. P-E & N-E was >299Mohms. I got 0.98Mohms on P-N but when I connected P&N together & measured across to Earth I got >299Mohms. I thought everything was unplugged but the house owner wasnt there & I wanst sure if an outside light had been spurred off a socket or something silly like that. Is this ok to put 0.98Mohms in the box & put a note saying P-N joined & tested across to E gave a >299Mohm reading.