You seem to have ruled out all the usual suspectls like loose connections, borrowed neutrals etc, so it must be something more obscure, so I may go off on a bit of a tangent here
You say the supply is T-N-CS. Is the network definatly PME'd? We have seen a few posts on here recently about DIY conversions from TT.
Have you tried taking a voltage reading between the installation earth and true earth? I'm wondering if there might be a failing joint on the neutral somewhere locally on the network?
I had an intermittent RCD trip fault a while ago. It was sometimes at random, and sometimes co-incided with a light being switched.
I took an incredibly poor quality video on my phone showing what I tracked the fault down to
You say the supply is T-N-CS. Is the network definatly PME'd? We have seen a few posts on here recently about DIY conversions from TT.
Have you tried taking a voltage reading between the installation earth and true earth? I'm wondering if there might be a failing joint on the neutral somewhere locally on the network?
I had an intermittent RCD trip fault a while ago. It was sometimes at random, and sometimes co-incided with a light being switched.