Who cares, the MK switches will have to be to BS 1363 to be used on the 'primary' circuit of the ring main anyway. Does anyone know if they are?What are BS 1363 accessories "rated at"?
Who cares, the MK switches will have to be to BS 1363 to be used on the 'primary' circuit of the ring main anyway. Does anyone know if they are?What are BS 1363 accessories "rated at"?
We 'had' this recently.Who says?Remember the switches are usually rated at 20amp, so cannot be used on a 32amp ring main without first being fused down.
What are BS 1363 accessories "rated at"?
Was not BAS's point that the switches in accessories (e.g. sockets) which undeniably are to BS1363 are probably usually rated at <32A, yet we happily use them in situations in which they are only 'protected' by a 32A OPD (not the least because of the presence of downstream fuses). I suppose that wouldn't matter to those who believe that the OPD is there only to protect cables (and hence that accessories do not require any 'protection'?)!We 'had' this recently. It's not the rating which is in question but the fact that 20A DP switches are actually NOT BS1363. I think the conclusion was we wouldn't worry too much if fitted but technically ...?Who says? What are BS 1363 accessories "rated at"?
Well yes, but that's a different matter, I think, in that it is only the actual terminals which have to cope with the current up to the OPD rating but even then the full current wouldn't actually flow through the terminals.Was not BAS's point that the switches in accessories (e.g. sockets) which undeniably are to BS1363 are probably usually rated at <32A, yet we happily use them in situations in which they are only 'protected' by a 32A OPD (not the least because of the presence of downstream fuses).
Because of the above, that may be true.I suppose that wouldn't matter to those who believe that the OPD is there only to protect cables (and hence that accessories do not require any 'protection'?)!
Indeed. In fact, virtually none of the 'ring' current should flow 'through the terminals' - only that going to the loads plugged into the socket.Well yes, but that's a different matter, I think, in that it is only the actual terminals which have to cope with the current up to the OPD rating but even then the full current wouldn't actually flow through the terminals.
Yes, I suppose that is true. I actually suspect that, rather than restricting accessories on a ring final to BS1363 ones (which, with its wording, it effectively does), the actual intent of 433.1.103 may have been to 'dispensate' the use of BS1363 accessories (probably rated at 13/20A) on a '30/32A circuit'. However, if that was the intent, they got the wording all wrong!I was pointing out that 20A DP switches are not BS1363 and so (in a recent thread it was argued that) they are/may/would not be allowed on a ring circuit but would be on a similar radial.
Indeed - but unnecessary as that would equally apply on a 32A radial.Yes, I suppose that is true. I actually suspect that, rather than restricting accessories on a ring final to BS1363 ones (which, with its wording, it effectively does), the actual intent of 433.1.103 may have been to 'dispensate' the use of BS1363 accessories (probably rated at 13/20A) on a '30/32A circuit'. However, if that was the intent, they got the wording all wrong!
You say 'quite clear', but it doesn't actually say "only BS1363 acessories" - hence my previous comment.However, it is quite clear - "BS1363 accessories may be supplied through a ring final circuit ..." - and 433.1.103 is about the CCC of the wiring.
I suppose that's simply because standalone switches are outside of the scope of BS1363. Again, I suspect that the 'fault' is with the wording of 433.1.103 in that it was not written to include them, even though they are subject to a different standard from BS1363. Maybe the person who wrote it didn't even know that they were outside of the scope of BS1363More puzzling is why the 20A switches are not to BS1363 and what difference that entails compared with an FCU which is.
As EFLI has said, the one's you linked to are not suitable, because they are not double-pole. If you can find 2-gang double-pole switches, then you could use them as you describe - but, again as EFLI has said, I think you might struggle to find them, except as grid switches.Just thinking out loud... can you use something like this http://www.electricpoint.com/switch...gle-shopping&gclid=CPzWqYv__LYCFYXItAodWV8ACA above counter, with each switch leading to a separate unswitched FCU under counter. At least that way I'd get 2 switches in one faceplate and no visible fuses.
If you use Double Pole switches like that then yes.
I think you may have to use a grid type.
No more than for any other item.Is there a restriction on where the grid/FCUs can go.