Hi Guys
Can I pick your collective brains once more, please?
I attended an RCD fault today. Has me a tad stumped.
Supply, TN-S with Ze of 0.16.
16th Ed. split-load board.
RCD tripping, but never, according to the customer, at night. Trips sometimes during the day without any obvious action preceding the trip, but trips every time when upstairs lights (usually several together) are switched on.
So it seems as if whatever is tripping the RCD it is related to a certain load on the upstairs lighting circuit.
However, the upstairs lighting is on the incomer side, not the RCD.
I have IR'd the board using method 2 & got 40 Meg. I realise this figure is not top-end, but neither does it seem to indicate any faults capable of tripping a healthy RCD.
I have tested the RCD and got 34/12ms & a ramp of 23.5mA.
The only obvious fault I've found at the board was that the main earthing conductor had dropped out of the 'bar. A Zs taken from a RF circuit was 0.5 prior to the conductor being replaced & 0.22 afterwards.
Help!!
Can I pick your collective brains once more, please?
I attended an RCD fault today. Has me a tad stumped.
Supply, TN-S with Ze of 0.16.
16th Ed. split-load board.
RCD tripping, but never, according to the customer, at night. Trips sometimes during the day without any obvious action preceding the trip, but trips every time when upstairs lights (usually several together) are switched on.
So it seems as if whatever is tripping the RCD it is related to a certain load on the upstairs lighting circuit.
However, the upstairs lighting is on the incomer side, not the RCD.
I have IR'd the board using method 2 & got 40 Meg. I realise this figure is not top-end, but neither does it seem to indicate any faults capable of tripping a healthy RCD.
I have tested the RCD and got 34/12ms & a ramp of 23.5mA.
The only obvious fault I've found at the board was that the main earthing conductor had dropped out of the 'bar. A Zs taken from a RF circuit was 0.5 prior to the conductor being replaced & 0.22 afterwards.
Help!!