With a standard kitchen/ bathroom fan arrangement, it is difficult to imagine how a significantly larger load could be substituted. However, in your cellar situation, potentially your spur off a spur arrangement could be used to supply (for example) a tumble drier and a washing machine.
It's unlikely (as would be apparent if you saw the location) but, I agree, theoretically not impossible. I would personally think that what you're postulating is just about the most extreme scenario one could reasonably anticipate (without getting very contrived). Do you agree?
If so, I would suggest that such an (extreme) scenario is within the design parameters of what I was talking about. The short 2.5mm² spur cable from the ring is clipped direct, so you would have to postulate a total load on the FCUs greater than 27A for an appreciable period of time before the cable's CCC was exceeded. OK, so some joker might wire 3 tumble driers into my FCUs, but that's a ridiculously contrived suggestion, and I can't honestly think of any remotely likely way in which a persistent load >27A would be connected, can you?
Of course, the specific situation can alter how the designer considers selection and erection of equipment. As you suggest, some scenarios are unlikely (or far less likely) to be abused and in theory you could ignore certain regulations without fear of creating a dangerous installation.
Agreed - but see above I don't believe that I actually
would be 'ignoring' (or violating) any regulations. What BS7671 says about ring final circuits, and, in particular, what is written in the ('informative') Appendix 15 about such circuits, merely relate to arrangements which are deemed to satisfy the underlying requirements of the regs - but a designer remains free to utilise other designs which satisfy those underlying requirements.
In the case under discussion, as far as I can see, the only issue is the possible oveloading of about 4 feet of 2.5mm² cable. However, as above, it is my opinion (and, dare I presume to suggest, probably also yours!) that it's incredibly unlikely that anyone would ever connect loads to that which drew more than 27A - so my opinion, as designer, would be that the design
does satisfy the requirements of BS7671 as regards the current carrying capacity of its cables under all conditions that can be reasonably anticipated. Do you disagree?
I think everyone carrying out electrical work owes it to themselves to consider how that installation may be used now and in the future and take that into account in the design and installation process.
As above, I believe that I
have taken into account all reasonable (and some pretty unreasonable!) possible future (mis)uses of the installation. Do you disagree?
Kind Regards, John.