(FSL) 2 cable 2k/4K7 as my setting then that is 2k2 as the eol and this determines secure or tamper, the 4K7 goes across the alarm pair (reed) to determine active zone.
The contact in your picture above is 4 wire.
red and black is the alarm pair and blue and yellow the tamper pair.
I can see from the manual, that the panel and older expanders require you to use the same wiring methods throughout.
so any sensor wired to the panel must use the same wiring type ie resistors if that is what you have selected.
If you have an expander you would have to check if you have the expander that is capable iof accepting mixed wiring types.
No expander
the keypad does give you an option of choosing what type for all then you can individually change them ie for the 2 door contacts will amend them to 2K2