securespark said:Wouldn't use Type C in domestic..........
This was also mentioned in the part p course
Your not supposed to use a type C rated CB in a domestic dwelling unless its extraordinary circumstances.
securespark said:Wouldn't use Type C in domestic..........
M1K3 said:securespark said:Wouldn't use Type C in domestic..........
This was also mentioned in the part p course
Your not supposed to use a type C rated CB in a domestic dwelling unless its extraordinary circumstances.
andrew2022 said:M1K3 said:securespark said:Wouldn't use Type C in domestic..........
This was also mentioned in the part p course
Your not supposed to use a type C rated CB in a domestic dwelling unless its extraordinary circumstances.
problem is, if the circuit is gonna trip everytime a bulb goes, then surely that circuit is not designed properly, and should have a type C
plugwash said:btw sometimes bulbs blowing can cause a huge surge of current. I had one in my inspection lamp take out a B16 (loft socket cuircuit) recently.
crafty said:But the circuit is designed properly, its the bulbs that are badly designed. Manufacturers know their products are going to be used on a 6 amp MCB or 3 amp fuse, and so should design their products as such in order to eliminate nuisance tripping.
Normal wall switches are allowed in Zone 3 or beyond.lorraine said:Bathroom Switch - I would like to leave this as if I take it out it will leave a massive hole in the wall and I can't get matching tiles from anywhere but I was aware that most bahtrooms had pull cords but was not sure if this was due to zonal arrangements or not.
You can have a socket it you want, as long as the socket is not intended, or could reasonably be expected, to supply portable equipment for use outdoors,Downstairs sockets are on an RCD, I am going to buy a cooker switch with no socket on for the cooker circuit as this won't be on the rcd side of my consumer unit.
You can spur.Do I have to provide a separate circuit for my boiler? Which hasn't been fitted yet (I had electric heaters before) or can I spur off the kitchen ring?
Not without proper test equipment, apart from gross L/N/E faults with a multimeterAlso are there any safety tests I can perform before the council comes round to check?!?
MCB Types: //www.diynot.com/forums/viewtopic.php?p=76467#76467I did not realise the difference between B and C type MCB's! I just went in the shop and the guy gave me a B. incidentally are there any A type?
Measure it. It's either in Zone 2 or it isn't.Fit a "Pull cord" switch, and fit a blanking plate in place of the existing wall switch, it's a lot cheaper than a revisit from the council
You should ask for your money back - they didn't teach you properly.M1K3 said:securespark said:Wouldn't use Type C in domestic..........
This was also mentioned in the part p course
Your not supposed to use a type C rated CB in a domestic dwelling unless its extraordinary circumstances.
And if you know that they do not, you deliberately design something inappropriate, do you, and shrug your shoulders saying "it's not my fault the MCB trips - the bulb manufacturers should make better products."?crafty1289 said:But the circuit is designed properly, its the bulbs that are badly designed. Manufacturers know their products are going to be used on a 6 amp MCB or 3 amp fuse, and so should design their products as such in order to eliminate nuisance tripping.
Shouldn't "presume".plugwash said:dunno i presume its a 3A one but it didn't blow so i had no reason to open up the plug to check.
I use GE GLS and R080 lamps - they take the MCB out every time....securespark said:GE GLS lamps have Ballotini fuses also.
The boiler should only cause the RCD to trip if the boiler developes a fault.lorraine said:I shall put the boiler onto a FCU but I was a bit worried that as the kitchen ring was on an RCD, that the combination of electrics and water in my boiler would result in some earth leakage and cause a trip.
As long at the cables are run in prescribed areas which it sounds like they are, there is no problem.Also while I'm atit is it permissable to cross cables? I am putting in 10mm cable for my cooker but this will come down the wall vertically. The easieist route for my kitchen ring is horizontally around the room and I was wondering if it was okay to cross the two at an accessory point or not?