forgot 2 say ure bypass should be a gate valve with a red handle situated in airing cupboard tee'd off before flow into the motorised valve/valves
wot u need 2 do is get the boiler working by pressing the rest button,stand and waite while its running,is there any gurglying noises??if so it may be air in system causing boiler to overheat??does the flow pipe get red hot after being on for only 20-30 secs???if so this would suggest circulation or pump issue???if the system was really sludged up did the plumber replace ne pipework in airing cupboard i.e air sep or h section????if he didnt then that could be cause as flush wont completly unblock a badly restricted air sep.only other thing is if the flow pipe isnt red hot and the over heat is still tripping then its a faulty o-heat stat.hope this helps u
forgot 2 say ure bypass should be a gate valve with a red handle situated in airing cupboard tee'd off before flow into the motorised valve/valves
You need to feel the TWO pipes from the boiler while its heating up.
If the pump is OK and the system not blocked then there will only be a skight difference of about 10° between the two pipes.
If the cool one is still almost cold then there is a serious flow/blockage problem.
I really cannot understand how anyone can come and powerflush without including dealing with any other flow problems on your system.
Tony
If you hear water sounds it seems its not filling properly.
Have you checked the F&E tank and run water off to see if the level falls? See FAQ.
Tony
forgot to ask,u said it o-heated after 18 mins????do all of ure rads get at least warm at this stage????if they are all getting warm then it cant be a circulation issue,do u find downstair rads poor??