So - what do you call current that is leaking to earth?
Lighting?
how much did you pay for it?
£35 with 1 mA resolution, OK maybe we should be able to measure 3.5 mA, but over 3 mA then should not be using single earth and 13 amp socket, do we really need to measure 3.5 mA?
That makes me think that you probably have more than one circuit which has some leakage.
Now we are talking, this is my point, we need to ensure it is the UFH at fault.
I luckily found when a builder had caught the UFH and twisted wires together and said nothing, unlikely his electrician would have found it, as he turned up without even an insulation tester, Part P had just come in, but it seems that electrician had not caught up.
We can pick people up for using wrong names, live instead of line, low voltage instead of extra low voltage, and yes there are times wrong names can throw one, but in the main, it hardly matters, I know I have a fault in my own house, before solar panels were fitted I had around 19 mA to differential, after about 8 mA to differential between the tails to the consumer unit, and the 3 freezers and central heating are now not fed from the consumer unit, so it does seem likely there is a fault somewhere, likely the central heating. It is on my to-do list, as is fitting a RCD FCU to the central heating supply. I left it as a summer job, so time to correct any faults. But without the clamp on, I would have no idea there was a fault, and since issued a compliance certificate if I was not an electrician would have not given the moving of the central heating to a non RCD protected circuit a second thought.
But does it really matter if called an imbalance, a differential, or earth leakage? We are not sitting an exam where they are trying to catch us out with phrases like "and others" which was with 17th the difference between skilled and competent.
Yes, something is causing an imbalance, and yes
Some older thermostats have a "heat anticipator" which is a mains powered resistor which gives out a small heat to improve the response.
and I have seen this connected to earth rather than neutral, but what we are looking at is a system where an electrician has tested it and found no fault, so one would hope errors like that would be spotted! Also see green/yellow used as a live wire, even seen it used as a line wire. "The bi-colour combination green-and-yellow shall be used exclusively for identification of a protective conductor and this combination shall not be used for any, other purpose." note full stop, but it continues "Single-core cables that are coloured green-and-yellow throughout their length shall only be used as a protective conductor and shall not be over-marked at their terminations, except as permitted by Regulation 514.4.3." and I have had people say therefore one can use the green/yellow core of a multicore cable! And over sleeve. They must have done a different English class to me?
We know we should not do it, they are clearly clutching at straws as they did not have four core on their van, however errors like that can escalate, one sees a green/yellow and instinctively connect it to earth, we simply don't expect some idiot to have used it as a live, even if used for neutral, the neutral is still classed as a live wire.
So yes that is one easy missed, but can't see how one would fail to find it with standard meters carried by electricians, if a plumber has attended (no slight on
@Agile ) I could understand how it could be missed, but we are told an electrician came.
So my money is on some other item being faulty, with an earth - neutral fault, and the load of the UFH is enough to raise the neutral voltage above earth enough for it to trip the RCD, problem is even turning off all the other MCB's will not help, as the MCB does not isolate, it only turns off the line, the neutral is still connected, as an electrician using a 500 volt mega (sorry insulation tester) it is so easy to unplug all items to ensure you don't damage it with the 500 volt, better to test with 250 volts and leave all connected, but for the householder that must be the first thing, unplug all you can, and switch off any switched FCU's (fused connection units) does it still trip?