Good afternoon,
I have finally saved some money to look at replacing my boiler (I have a limping wounded Heatline Capriz28 which needs to be gracefully retired after 7 years service) and need to look at what size i need so i can check the models available, review them and see what deals are around and about!
So i did a boiler size on my 3 bed semi (see below) with now added extension (knock through kitchen/dinner, utility and downstairs shower room so taking that in to account) and it comes back as boiler out put 26.8kW so anything around 28/30kW would be good as i am fitting mains showers in both bathroom and shower room?
Whole House Boiler Sizing Method - Results
Job Reference: 25 March 2013 13:32
Area Calculation
Length (m) 13.0
Width (m) 9.0
Height (m) 4.0
No. of floors 2
No. of walls width-wise 2.0
No. of walls length-wise 1.0
Calculated wall area (sq m) 248.0
Wall and Window Heat Losses
Dwelling type Semi-detached
Window area 49.6
Window type Double glazed wood/plastic
Window heat loss (W/deg) 148.8
Wall type Filled cavity wall
Wall heat loss (W/deg) 89.2
Roof and Floor Heat Losses
Roof area 117.0
Floor area 117.0
Roof insulation Pitched < 50mm insulation
Roof heat loss (W/deg) 304.2
Floor heat loss (W/deg) 81.8
Fabric Loss
Wall+window+roof+floor heat loss (W/deg) 624.1
Location North & Midlands
Calculated fabric heat loss (W) 18101
Ventilation Loss
Calculated volume (m3) 936.0
Location factor 29.0
Ventilation heat loss (W) 6786
Calculate Boiler Output
Calculated total heat loss(W) 24887
Add for water heating (W) 2000
Add for extension or other (W) 0
BOILER OUTPUT (kW) 26.8
I've read that putting in a larger than needed boiler not only costs more but would be dearer to run is this right?
I've been quoted a Valiant EcoTech Pro 28 with flue for just under £700 which i think is pretty good value and think would be fine but would i be best getting the next one up in case i convert the attic?
Cheers
Pete
I have finally saved some money to look at replacing my boiler (I have a limping wounded Heatline Capriz28 which needs to be gracefully retired after 7 years service) and need to look at what size i need so i can check the models available, review them and see what deals are around and about!
So i did a boiler size on my 3 bed semi (see below) with now added extension (knock through kitchen/dinner, utility and downstairs shower room so taking that in to account) and it comes back as boiler out put 26.8kW so anything around 28/30kW would be good as i am fitting mains showers in both bathroom and shower room?
Whole House Boiler Sizing Method - Results
Job Reference: 25 March 2013 13:32
Area Calculation
Length (m) 13.0
Width (m) 9.0
Height (m) 4.0
No. of floors 2
No. of walls width-wise 2.0
No. of walls length-wise 1.0
Calculated wall area (sq m) 248.0
Wall and Window Heat Losses
Dwelling type Semi-detached
Window area 49.6
Window type Double glazed wood/plastic
Window heat loss (W/deg) 148.8
Wall type Filled cavity wall
Wall heat loss (W/deg) 89.2
Roof and Floor Heat Losses
Roof area 117.0
Floor area 117.0
Roof insulation Pitched < 50mm insulation
Roof heat loss (W/deg) 304.2
Floor heat loss (W/deg) 81.8
Fabric Loss
Wall+window+roof+floor heat loss (W/deg) 624.1
Location North & Midlands
Calculated fabric heat loss (W) 18101
Ventilation Loss
Calculated volume (m3) 936.0
Location factor 29.0
Ventilation heat loss (W) 6786
Calculate Boiler Output
Calculated total heat loss(W) 24887
Add for water heating (W) 2000
Add for extension or other (W) 0
BOILER OUTPUT (kW) 26.8
I've read that putting in a larger than needed boiler not only costs more but would be dearer to run is this right?
I've been quoted a Valiant EcoTech Pro 28 with flue for just under £700 which i think is pretty good value and think would be fine but would i be best getting the next one up in case i convert the attic?
Cheers
Pete