MEM, Seimens, Merlin-Gerin/Schneider, .... ?
Is contactum a good brand?
Not considered the best. Cheap though and a 25 year guarantee on their accessories if they manage to exist for that time. They went into administration a couple of years ago but were bought by a Saudi firm, I think. Wouldn't be as confident that their CU stuff would be as easily available as MK, Hager, Wylex for example.
MEM, Seimens, Merlin-Gerin/Schneider, .... ?
With the caveat that I am not an electrician .....What is the reason for the large and moderately expensive bit of kit known as a switch fuse? The armoured cable terminates into it, and tails feed it from the henley block. Specifically, what is the advantage over the upstream isolator (one is being put in before the Henley block), which has no fuse but as I understand it does the same job of disconnecting the current in the event of disaster? I was under the impression fuses could now be replaced by handy little devices without any replaceable parts.
Including financially, because it would mean that the SWA would have to be sized to be OK on a fuse the size of the DNO one.... and the DNO's fuse is usually allowed to protect no more than 2-3m of meter tails. If there was no switch-fuse for the SWA, then that entire length of SWA would have no overload or s/c protection other than the DNO's fuse, which would be bad on a number of levels.
The reason that a fuse is preferred is to give better discrimination, i.e. that a fault in a final circuit in the garage will just trip the MCB in the garage CU, not take out the upstream device. If the upstream one was an MCB there would be little or no guarantee of that.I was under the impression fuses could now be replaced by handy little devices without any replaceable parts.
Including financially, because it would mean that the SWA would have to be sized to be OK on a fuse the size of the DNO one.... and the DNO's fuse is usually allowed to protect no more than 2-3m of meter tails. If there was no switch-fuse for the SWA, then that entire length of SWA would have no overload or s/c protection other than the DNO's fuse, which would be bad on a number of levels.
The OP seemed to be saying that there was an upstream 'isolator' which incorporated overcurrent protection, prior to the splitting of the tails. If that's true (sounds slightly odd to me), then that device (not just the DNO's fuse) would be protecting the split tails. However, as I said, that would obviously mean that the device would have to be rated for the entire installation, far too high to protect the SWA (unless ludicrously large/expensive SWA were used!).... and the DNO's fuse is usually allowed to protect no more than 2-3m of meter tails.
Perhaps I shall do a part P course myself and hit the road with my trusty neon screwdriver icon_wink.gif
Ah, then maybe it is just as isolator then (a manually-operated 'switch' in common parlance, although unlike switches, an isolator is not intended to be used to switch off a circuit 'under load'). It could well be that the electrician has specified an isolator there to faciliate his subsequent work (and that of other electricians in the future). What made me think that you knew it afforded overcurrent protection was that you wrote:I don't know if the planned isolator provides overcurrent protection or not, it's just labelled 100A double pole isolator on the diagram.
...the upstream isolator (one is being put in before the Henley block), which has no fuse but as I understand it does the same job of disconnecting the current in the event of disaster
Indeed. I thought you were primarily asking why the switch fuse (or some alternative) was there at all (given the presence of the upstream 'isolator'), with the fuse vs. MCB question as a 'secondary' one.My intended question would perhaps have been more clearly put as why a switch fuse for overcurrent protection instead of a cheaper, smaller modern circuit breaker. Either could be rated at a level to protect the cable downstream. I think BAS's answer covers it with discrimination.