Just thought I'd update everyone on the current situation. After a lot more pressure on the developers, they've sent over the NICEIC certification again which they claim proves that the wiring was sufficient at 1.5mm².
We are now stuck again as our electrician claims 2.5mm² is necessary and 1mm² was installed whilst the developers say that 1.5mm² was installed and sufficient. Since they have their certificate, they are satisfied they've done nothing wrong despite the wiring melting. Everyone here has been extremely helpful. Is there a correct answer?
We are now stuck again as our electrician claims 2.5mm² is necessary and 1mm² was installed whilst the developers say that 1.5mm² was installed and sufficient. Since they have their certificate, they are satisfied they've done nothing wrong despite the wiring melting. Everyone here has been extremely helpful. Is there a correct answer?