New shower not heating up hot.

Joined
5 Feb 2007
Messages
1,099
Reaction score
15
Location
Liverpool
Country
United Kingdom
I have had a new 8.5kw shower installed.

It is installed with 6mm cable clipped with a 32 MCB.

The shower is getting warm but not hot.

Could it be the fuse needs changing t0 a 40 amp as 8.5kw is roughly 37 amp ?

Would the shower still not get hot but trip if this was the case so I suspect a fault with the shower ?
 
Last edited:
Sponsored Links
What device rating does the MI say the shower needs?
And what voltage rating is the power/current being calculated?

Also the voltage drop and method of installation must be factored into this, it is possible that a 6mm T&E cable cannot be safely protected by a 40A device.
 
Last edited:
Would the shower still not get hot but trip if this was the case so I suspect a fault with the shower ?
I have seen showers rated at 8.5kW run on a 32A breaker without tripping it.
It would depend on how long the the overload is allowed to continue, to if the device will trip.
 
Sponsored Links
Changing the MCB will make no difference to how well the shower heats the water. MCB will either permit current to flow or will trip- a 32A MCB supplying a 40A load won't 'throttle' the supply to 32A- it'll pass 40A for a while and then it'll trip.
 
Back
Top