I have waited to see what develops in this thread, because I do not understand what the alleged problem was, and some of the replies are drivel.
The facts of the matter are as follows:
The current Vitodens 100-W 30kW combi will raise 12 litres/minute of water through 35deg. If the incoming mains water is at 10C, you will get 45C out. If the incoming water is at 5C, you will only get 40C, just above blood heat. If you want a higher temperature, just reduce the flow rate a bit at the tap. Naturally, it will be better in summer. We have just had the coldest winter in living memory, and the water is very cold just now.
The gas pressure required is 17.5mb at the inlet to the multifunctional gas valve, and the supply pipe needs to be sized to suit. A qualified installer will know how to calculate the pipe size. The gas consumption will be 3 cubic metres/hour at full output.
Hi MM,Thanks for your reply.Since my post above, I have received a visit from my RGI,and The sales Manager from Veissman, who happens to be a personal friend, time served gas engineer, knows what he,s talking about.He did a thourough check of installation,pressures, cold water temp, hot water temp @ 12 litres pm, and got 43.5c, well within the manufacturers parameters.The boiler is working fine, not nescessary to upgrage the pipework, exactly as RGI stated at time of instalation, and asimilates to what you have just quoted.The Engineer who stated pipework needed upgrading, I,m afraid is in for a balling out.1, He gave me his personal card, both RGI and Manager wanted to know why? I presumed it was ID, alas, there is more to it than meets the eye.He shouldn,t have, my only contact should be through RGI or Veissman.he was here 15 mins, they were here an hour.The reason the RGI called the Engineer was because the boiler shut down 3 times @86.2c,thermal cut out,with no fault sign showing.He didn,t/couldn,t explain why, but neither could the others.The only reason I can deduce from all this is that the first Engineer was trying to get HIMSELF to upgrade the pipework unnescessarily, bypassing the original RGI.Apparently it seems it,s not the first time this Engineer has come under scrutiny.It,s certainly upset both the RGI and the Manager, as it,s casting doubts on RGI workmanship, which the Manager Et Al said was second to none before I hired him.I didn,t just get him from yellow pages,I contacted friends who had used him.All,s well that end well.I thank all for their input, specially Tony again.