There are two requirements!
A proper auto bypass valve set at about 0.3 bar which will normally be closed until most of the TRVs start to close.
Then, perhaps, a manual bypass in parallel with the auto bypass to set a SMALL amount of bypassing to aid increasing the return temperature to help the boiler in ramping up when starting from cold.
If I had a moment then I would check further on the latest Viessmans with the return sensor. But this feature does give a bit of a problem on Vaillants if the return temperature does not rise soon after start up as can happen on larger systems.
If you were to monitor the flow and return temps during start up then it would give a bit more information on what is happening.
Tony
A proper auto bypass valve set at about 0.3 bar which will normally be closed until most of the TRVs start to close.
Then, perhaps, a manual bypass in parallel with the auto bypass to set a SMALL amount of bypassing to aid increasing the return temperature to help the boiler in ramping up when starting from cold.
If I had a moment then I would check further on the latest Viessmans with the return sensor. But this feature does give a bit of a problem on Vaillants if the return temperature does not rise soon after start up as can happen on larger systems.
If you were to monitor the flow and return temps during start up then it would give a bit more information on what is happening.
Tony