baxi solo boiler - new control board, gas valve- boiler gets hotter and hotter but not pipes - pump runs- HELP, getting expensive now.... water makes rushing noise regularly :?:
 
Sponsored Links
somewhere around the highest point of the system there will be an air bleed in the pipework on a vertcal bit of copper, open him up and bleed the air out. That's the first point of call anyway.
 
system has now been bled..... still no joy....what now ... someone has told me either thermostat or blocked coil. how do i check?
 
thought I'd answered this. Revisit the pump - could be spinning but not pumping. Impellors can come loose , and they can go slow.

Feel the pipes to see how far the hot water gets.
 